Title: Busbar It and operating temeratures
Post by: thood.bsec on 07 June 2024, 10:50
I have noticed that bus bar actual operating temperatures are showing as exceeding 70 degrees when design currents are less than half the bus bar rating Iz.  The software also applies a 0.86 Ct correction factor to the bus bar for 70 degree operating.

Q1: Why would the bus bar exceed its rated operating temperature before its rated It is reached when no correction factors need be applied?
Q2. Why would the software de-rate the bus bar to operate at 70?

There is lots of information on design in the Schneider catalogue including specific de-rating factors for ambient temperature and CPD type but there is no de-rating when installed in ambient of 35 or less and protected by an MCCB (my install).

(https://i.postimg.cc/DJR8bk8B/image.png) (https://postimg.cc/DJR8bk8B)
Title: Re: Busbar It and operating temeratures
Post by: admin on 07 June 2024, 11:11
Hi,

The Ct factor only applies to the voltage drop calculations in Appendix 4 in BS767.

The software checks based on the limit specified by the user. In your case 70oC. Please see the image below too
(https://i.postimg.cc/qtvTZrQ5/max-temp-spec.jpg) (https://postimg.cc/qtvTZrQ5)