Canalis Busbar Missing

Started by RCDGuy, 05 October 2021, 13:54

Previous topic - Next topic

RCDGuy

I'am installing Canalis (Schneider Bus-Bar) range KNA63ED4306 but am unable to locate this on the system, can this be added and also other types of Canalis.

Also on Plan design where are the symbols for the different types of containment???

Mert

The KNA range is aluminium busbars so you need to select the Al - Aluminium conductors option. Then it will list the aluminium rage including KN. See the screenshot for help.

In plan there is no any specific symbols for containment. Of course you can create one but usually is better to use muli-lines or just polylines with a specific line type. See the screenshot for some samples






RCDGuy